When connecting aluminum service conductors to a breaker panel do I need to use - Printable Version +- Forums (https://askaluminium.com) +-- Forum: My Category (https://askaluminium.com/forumdisplay.php?fid=1) +--- Forum: aluminium faq (https://askaluminium.com/forumdisplay.php?fid=2) +--- Thread: When connecting aluminum service conductors to a breaker panel do I need to use (/showthread.php?tid=32768) |
When connecting aluminum service conductors to a breaker panel do I need to use - RogerTib - 01-13-2020 On Square-D service panels, are the main lugs rated for aluminum wire? Or do I need to use an anti-oxidant compound? What about on Milbank outdoor meter bases?Aluminum to Aluminum they say you do not need an inhibitor. I have still aways used it as has every electrical contractor I have worked for for 30 years. Utility companies use it on all meter bases as well. The oxidation can still be persistent so I suggest you use it and torque them to the manufactures labeling. So many people over tighten the conductors and this is a major problem because aluminum is very soft it does have a torque guideline for each conductor size as well as the lug it is attached to. Electrical Contractor ||No you do not have to use any type compound on it.Other related question
|